Not today, but several years ago. Could be of interest though.
Fireplace outfit that I used to help out occasionally with tech stuff. The did marble surrounds, woodstoves etc I occasionally built non standard wood stoves for them, like a six sided one for a restaurant.
They got into underfloor electric heating, using kit from Holland or scandi.
Anyway, a big living room had been wired and the floor laid with very expensive tiles. The system tripped out to earth and hair was being pulled at digging it up, around 80 sq mt. so a lot of money.
Talking to the factory, they had a bit of kit to find the fault and sort it, so sent it out. Interesting box arrived. The cabling was +ve & -ve twin and the idea was that the machine ran 4,000 volts down the wire and then at the damaged point, it would carbonised the insulation. It then sent a low pulse down the line and one used a detector to follow the the line until the pulse stopped, which would be the point were the cable shorted.
I read the book carefully and we tripped out to the house (a new build and very smart..) and got to work. Owner was there too....
Ran the system with the high voltage (carefully!) and checked the pulse system. Seemed to function, so started with the detector and phones.
After going backwards and forewards over most of the floor, the pulse stopped. Confirmed it with a few passes, then chalked a cross and told the waiting bloke with the tools to dig there. He bust up the tile and chiselled the concrete. Few minutes later a charred cable appeared within an inch of my cross. The atmosphere of relief was pretty solid and the owner extremely impressed. The box had come with repair kits and I fitted one, potting the result, then tested the system, all OK.
I also commented that likely, from the look of it, someone had leaned on a spade and cut the insulation.
They bought their own tester box and applied new MO. Systems were tested after laying and again after concrete laid. After that, any fault was charged to the builder.
KF
Fireplace outfit that I used to help out occasionally with tech stuff. The did marble surrounds, woodstoves etc I occasionally built non standard wood stoves for them, like a six sided one for a restaurant.
They got into underfloor electric heating, using kit from Holland or scandi.
Anyway, a big living room had been wired and the floor laid with very expensive tiles. The system tripped out to earth and hair was being pulled at digging it up, around 80 sq mt. so a lot of money.
Talking to the factory, they had a bit of kit to find the fault and sort it, so sent it out. Interesting box arrived. The cabling was +ve & -ve twin and the idea was that the machine ran 4,000 volts down the wire and then at the damaged point, it would carbonised the insulation. It then sent a low pulse down the line and one used a detector to follow the the line until the pulse stopped, which would be the point were the cable shorted.
I read the book carefully and we tripped out to the house (a new build and very smart..) and got to work. Owner was there too....
Ran the system with the high voltage (carefully!) and checked the pulse system. Seemed to function, so started with the detector and phones.
After going backwards and forewards over most of the floor, the pulse stopped. Confirmed it with a few passes, then chalked a cross and told the waiting bloke with the tools to dig there. He bust up the tile and chiselled the concrete. Few minutes later a charred cable appeared within an inch of my cross. The atmosphere of relief was pretty solid and the owner extremely impressed. The box had come with repair kits and I fitted one, potting the result, then tested the system, all OK.
I also commented that likely, from the look of it, someone had leaned on a spade and cut the insulation.
They bought their own tester box and applied new MO. Systems were tested after laying and again after concrete laid. After that, any fault was charged to the builder.
KF