Yes @WorkshopChris 2.5 mm 1 m from the consumer unit and its the 4 kw 5.5 hp modelTheoretically 1hp should work on a good supply 2.5mm min. with 13a. If it is the smaller Static converter.
Yes @WorkshopChris 2.5 mm 1 m from the consumer unit and its the 4 kw 5.5 hp modelTheoretically 1hp should work on a good supply 2.5mm min. with 13a. If it is the smaller Static converter.
No not a loaded motor, not even installed its to try and ensure we have the Transwave working correctly before installationhum that is a bit close on 13A plug! especially on a loaded motor, the inrush could be a lot higher.
maybe not toooo bad, if on a clutched tool ?
The one linked to is not suitable as it's an undervoltage relay.Please forgive my total ignorance, im an Engineer Surveyor for Zurich Engineering on the Lift/Crane side the only electrical element of my inspections is for obvious damage/
burning/connections in say a lift panel or tripping limit switches, so does the lack of an adjuster on the item @normspanners kindly provided a link to not matter as it covers
the full range ?
Yes @WorkshopChris 2.5 mm 1 m from the consumer unit and its the 4 kw 5.5 hp model
The one linked to is not suitable as it's an undervoltage relay.
Also it would help to know what the current relay is switching, as Bryce appear to be the only ones to do 8amp rated contacts. They have another model in their range which would do - this one...
http://uk.rs-online.com/web/p/monitoring-relays/2989400/
But it's also unfortunately out of stock in rs!! The others that have suitable sensing ranges have lower rated contacts - if your not switching 8amps then you could use one of these, otherwise you either wait for the Bryce ones to come back in stock or use one of the smaller rated ones to switch an intermediate heavier duty relay to switch your final load.
Yes I believe it only works with the one contactor @daleydLooking at the pictures again it only seems to be operating the contactor next to it? If so then a smaller rated unit should suffice, but best to check.
Thanks @WorkshopChris it is fed from a sub board but the 1 m cable from the house is 4mm, the 1hp motor is for test my CVA lathe will be on a 4hp motor, my electrician is going to loadOk Although you are only running a 1hp motor, this bigger unit will have a larger transformer so your 13A Fuse may be issue.
Is the 1m from the consumer unit a main board fed from the suppliers meter or a sub board fed via a cable.
As this may need to be taken in consideration depending on size.
As a rule the bigger the cable the better for a converter once running they draw little power it the in rush and volt drop when starting.
Right off out to the workshop to check !!Just follow the cables from the voltage sensing relay contacts to wherever they go. If they only go to that contactor then I reckon your into a winner as it'll only pull a small amount of current, so you could get away with a smaller monitoring relay. If it powers other stuff then it gets trickier!
Ah just seen your post above as I'm typing! - if it's only the one contactor then you should see some info on the side of it telling you about power consumption. With this you can determine the size of relay you need to switch it.
Hi, this relay looks like it will do exactly what you need @Simon Melton.
It may well be a bit overkill for your application, but it's the only one I can find that matches the broyce unit specs and is in stock in RS. (240 v single phase supply and separate monitoring up to 300v - this one actually goes to 600v but you can select the range to suit). It looks to be very adjustable so you should be able to set it up exactly the same. The data sheet is very good and explains in some depth the operation modes etc. The output relays are rated to 5A rather than 8 but as you are only using it to drive the one contactor it should be OK.
http://uk.rs-online.com/web/p/monitoring-relays/8193295/
You may be able to source them elsewhere for cheaper than RS prices but these things are quite specialist so might be hard to source. (There are loads of single phase voltage sensing relays about but not many that will sense up to 300V, normally they just sense a % above their supply volts)