No one will sign it off with mixed manufacturers installed in a fuseboard.
Either split the tails into a switch fuse or.
Do as you originally stated, but 10mm swa is only rated at max 60a ref method D so I would say typeC 50a MCB in the house fuseboard and then go all RCBO in the garage fuseboard same as the house, they are not expensive and will stop everything going off if one thing developed a fault.