Thanks that would have been done by a pro sparky AFAIK a few years ago and was about to copy his install now but see what you mean about using swa glands.BS951 earth clamp.
But it shouldn't be on that SWA cable, this would earthed through a proper SWA gland!
Yes, its what I thought'It's always been a no no as long as I have been in the trade.
Yes constant force springs or sweated earth tail are compliant on a main incoming supply cable.
SWA cables it's always been a gland and earth tag (banjo) or now earth nut or wiska spring tag.
Even if the enclosure was plastic, you would just use two locknuts and sandwich the banjo between them!
correct no matter when it was fitted or by who its wrong its not a proper mechanical connection .a proper swa gland should be fitted with the earth tag and a brass nut and boltIt's always been a no no as long as I have been in the trade.
Yes constant force springs or sweated earth tail are compliant on a main incoming supply cable.
SWA cables it's always been a gland and earth tag (banjo) or now earth nut or wiska spring tag.
Even if the enclosure was plastic, you would just use two locknuts and sandwich the banjo between them!
Out of interest, what type of gland/brass nut bolt are you considering, thinking of?correct no matter when it was fitted or by who its wrong its not a proper mechanical connection .a proper gland should be fitted with the earth tag and a brass nut and bolt
But isn't that type of gland for fixing in to a metal or plastic CU for example, if I'm understanding photo, the striped sheath, ( the exposed armour ), is before that, how are you going to attach, fit it?
Not sure how you fit a CFS, have read they can be a bitch to fit.
on the end of the armoured not part of the way down it. just tape up the exposed wire coresBut isn't that type of gland for fixing in to a metal or plastic CU for example, if I'm understanding photo, the striped sheath, ( the exposed armour ), is before that, how are you going to attach, fit it?
How is it done, do you uncurl it, make sure the braid strap is in position, let go and it curls back up and clamps?You've got to watch your fingers when fitting them!
They are very springy and the edges can be sharp.How is it done, do you uncurl it, make sure the braid strap is in position, let go and it curls back up and clamps?
But isn't that type of gland for fixing in to a metal or plastic CU for example, if I'm understanding photo, the striped sheath, ( the exposed armour ), is before that, how are you going to attach, fit it?
It is indeed correct to say the above photo is/was never the correct method although I have come across many older installations just like this with this type of Earth Strap around the SWA and I suppose it depends on the various DNOs to ignore or get stroppy on such things if they happen upon them.
It's wrong anyway but if it's going to be done an external Tenby type strap should be used not the internal type, they look the same.
My understanding is a sweated leaded Earth Gland with a braided Earth strap was the norm, ( where the sheath had been trimed a little further down the SWA ), these can break/weaken/corrode over time hence the Tenby type clamps .
Thanks, you are correct, I was getting confused, I had in mind lead sheathed that has an Earth connection sweated on to them. I have seen many where the braid has corroded or the sweated connection has been broken and so a clamp of various kinds has been used.It has nothing to do with the DNO, their responsibility ends at the supply cut-out. You may be confusing the above picture of SWA with the lead sheathed type cables used by the DNO in the past which also are quite often seen with an earth clamp on them.
It would be just as wrong to use Tenby as it would any other manufacturers earth clamp, the only thing that would slightly improve it would be to fit metal tube under the armour so that it clamps the armour tightly.
Sweated/plumbed/wiped connections are used on lead sheathed cables, they are made by fitting the cable into a wiping cone and applying molten lead to it to connect and seal the joint, this is formed into shape by a process of wiping with a moleskin cloth (hence being known as a wiped joint). These connections aren't particularly prone to any weakening or corrosion.