I'm the one who said my hot water tanks only have 14kw coils, not op
what about that shows a lack of understanding ?
OP said he's going to fit the phe to the cold feed into the boiler, heated by the return from the coil in the tank... so it'll only be heated when the tank is, it'll start/stop with the tank coil feed as the tank stat calls for heat
also, it's an oil boiler so I can't see how it counts as uncontrolled ? (not like a wood burner etc.)
The max amount of heat the coil can transfer is 14Kw
If you fill the tank with cold water it will take X amount of time to heat up
If instead fill the tank with warm water from a plate heat exchanger then that time will be reduced as have to stick in less energy to reach the temperature.
If i could magically replace the 14Kw coil with a 36Kw coil then would you have an issue with that?
How is it an uncontrolled heat source when the heat exchanger is going to be fed from the outlet of the tank heating coil which is controlled by a zone valve?
The boiler itself has a normal thermal cutout for operating and an over temp cutout so that is another 2 layers of control.
The 14kw is used to calculate the size of the boiler and nothing else, give it 14kw and it will recover in 20 minutes, and heat from cold in 30-40, doesn’t mean it’s undersized
A boiler stat can fail and the overheat will be 105 deg c, anything over 90 is classed as uncontrolled. It also isn’t guaranteed to have a manual reset overheat, if it’s auto that’s not allowed either
Give it 14kw and it will recover in 20 minutes,
Those stats are not energy cut outs
Now just a thought, on my tank coil, std ish vented system, I have a gate valve on the return to act as a restriction to the flow to stop the boiler circulating the water too quickly and stop hysteresis, might he have a similar valve that might restrict the flow ?would also give you an idea if there's a problem with the flow rate etc. etc.
Yes as said, hysteresis, that is why I have a control valve on mine to stop that happening.faster the flow the quicker that heat gets back to the boiler shutting it down