Ok yeah I think your right then I know how.to check for continuity but that's about it with a meter
In this instance yes that will (should) be the return up to the neutral bar.I'm puzzled with the black wire link at the bottom left of the picture...……... is that correct ?
Yeah it's the output to the neutral connections at the topI'm puzzled with the black wire link at the bottom left of the picture...……... is that correct ?
Yes would by the parts but I wouldn't be able to fitFor less than £50 you could replace that lot with a new unit and properly glanded cables.
There are only 45amps worth of breakers the main is 63 so how did you burn it out ?
But the individual trips are off so pOwer shouldn't pass them when I turn on mcb
Ps, if you die we were never hear and know absolutely nothing.P.s if I die the misses has the log in details