This is a 3kw motor. ..If the full load current of the motor is 6 amps and your having to adjust the overload to 10 amps then there is something wrong, I'd suggest a clamp meter as above. No need for anything fancy, most cheapies will read close enough. Also what's the load on the motor, if it's got a lot of inertia then you can be limited by the number of starts (the windings get hot due to the starting current) , unlikely on a small motor but I've had overloads trip on large fans with a couple of starts in a row.