It's set at 10 when we are running it. If it's set lower than 10 it just trips quicker. And you confirm what I was reading that the motor is only 6What is the overload set at in photo 4 i cant make it out from the photo. Motor data plate has 6 amps. Is this a new bit of kit to you or has it just developed a fault. If it's a new bit of kit might just need the overload adjusting to suit new supply. Can you put a clamp meter on it at startup.
AH so that is possible thenOk so as the static phase converter has a 415v output the motor is wired correctly.
So now I'm thinking the motor is drawing more current on start up due to being ran from the converter, which is causing the overload to trip. So you need to turn the overload up, ideally by measuring the curren with a clamp meter and setting the overload accordingly.
Talking about clamp meters is a 25 quid on of ebay ok or does it HAVE to be a fluke?Ok so as the static phase converter has a 415v output the motor is wired correctly.
So now I'm thinking the motor is drawing more current on start up due to being ran from the converter, which is causing the overload to trip. So you need to turn the overload up, ideally by measuring the curren with a clamp meter and setting the overload accordingly.
What is the correct name of this switch please
What is the correct name of this switch please.View attachment 82347 View attachment 82348
Yeah I read that when I sourced my own converter. Especially lifts for some reason.It's a DOL (Direct OnLine) starter.
It strikes me that 10 seconds is a long tiime for a motor to spin up to full RPM (and thus be still taking start-up current).
My mate has a 4-post lift and bought a TransWave to power its hydraulics; the pump wpuld barely try to start even though the rating of the TW was higher than the pump's motor. He did some research and found that it wasn't recommended by the makers for that purpose so he had to buy a humungous one which does now work... but it cost him a bomb.
Even cheap AC clamp meters are as accurate as you need; I have a £17 B&Q special that is within fractions of a percent of my AVO across its range (we do instrument calibration at work so easy to check). It's only if you need DC measurement that the price goes up.
If the full load current of the motor is 6 amps and your having to adjust the overload to 10 amps then there is something wrong, I'd suggest a clamp meter as above. No need for anything fancy, most cheapies will read close enough. Also what's the load on the motor, if it's got a lot of inertia then you can be limited by the number of starts (the windings get hot due to the starting current) , unlikely on a small motor but I've had overloads trip on large fans with a couple of starts in a row.