Evening all! I have a question or two about a 16 amp supply. I found a thread but didn't quite answer my questions.
I was going to PM Brightspark as he seems to know his stuff. How can i PM him? Or can anybody else help?
I have an old storage heater consumer unit (3 fuses) which now only feeds a supply (via 6mm T&E though just one of the fuses) to the garage where there is a modern CU with RCD protection.
1) I am going to add a 16amp type 'c' MCB in the garage CU (for a table saw). The CU manufacturer said its fine with the CU i have… but is there anything else i need to worry about or is it ok to pop that MCB in?
2) I am running a cable from the 16 amp MCB to the 16 amp socket (just the one socket). What is the advisable cable size? I believe 2.5mm is sufficient, but is it better to run a thicker cable if i have the option?
3) I want to replace the old CU in the house with a new one to get rid of the wire fuse. All i have seen so far is 'shower CU' which all have an RCD and a single breaker, or garage ones which have a couple MCBs. Would i be better putting in just a 'on/off' breaker (called a DP?) as i have an RCD down stream at the CU in the garage. P.s. i will not be doing this bit myself! I am getting a sparky down to just hook up and test, but want to be as prepared as possible to save on the pennies!
I was going to PM Brightspark as he seems to know his stuff. How can i PM him? Or can anybody else help?
I have an old storage heater consumer unit (3 fuses) which now only feeds a supply (via 6mm T&E though just one of the fuses) to the garage where there is a modern CU with RCD protection.
1) I am going to add a 16amp type 'c' MCB in the garage CU (for a table saw). The CU manufacturer said its fine with the CU i have… but is there anything else i need to worry about or is it ok to pop that MCB in?
2) I am running a cable from the 16 amp MCB to the 16 amp socket (just the one socket). What is the advisable cable size? I believe 2.5mm is sufficient, but is it better to run a thicker cable if i have the option?
3) I want to replace the old CU in the house with a new one to get rid of the wire fuse. All i have seen so far is 'shower CU' which all have an RCD and a single breaker, or garage ones which have a couple MCBs. Would i be better putting in just a 'on/off' breaker (called a DP?) as i have an RCD down stream at the CU in the garage. P.s. i will not be doing this bit myself! I am getting a sparky down to just hook up and test, but want to be as prepared as possible to save on the pennies!