I took the lid off my 3 phase consumer unit and was a bit stunned by what I found...
The three phase is all reasonable, but the single phase circuits are all over the place. In one set of half a dozen power sockets, they appear to be connected across the three phases, which is not very sensible. The lighting circuit is also fed from one of the phases via a 6 mcb. There is no RCD protection either, despite a three phase, 13A and 16A socket installed externally so I want to sort it all out.
The CU is a MEM unit which modules are less common for, so my idea is as follows...
Leave all the three phase as is (not sure about RCD for the external 3p socket?) and take a feed from either a 40A or even the 63A mcb which is in there, to a new 18th CU with one or two RCDs and then feed all the single phase stuff exclusively from there. I have seen this one (only one at a realistic price!) and would appreciate comments. I would be happy with a 17th plastic CU but of course nobody is selling them, even though I did the installation years ago of course.
Feed from the 63A or the 40A mcb? Short length, perhaps 1m, so 6mm cable?
The three phase is all reasonable, but the single phase circuits are all over the place. In one set of half a dozen power sockets, they appear to be connected across the three phases, which is not very sensible. The lighting circuit is also fed from one of the phases via a 6 mcb. There is no RCD protection either, despite a three phase, 13A and 16A socket installed externally so I want to sort it all out.
The CU is a MEM unit which modules are less common for, so my idea is as follows...
Leave all the three phase as is (not sure about RCD for the external 3p socket?) and take a feed from either a 40A or even the 63A mcb which is in there, to a new 18th CU with one or two RCDs and then feed all the single phase stuff exclusively from there. I have seen this one (only one at a realistic price!) and would appreciate comments. I would be happy with a 17th plastic CU but of course nobody is selling them, even though I did the installation years ago of course.

Feed from the 63A or the 40A mcb? Short length, perhaps 1m, so 6mm cable?