I think you’re misreading the table on pg42. It states the minimum thickness of non combustible materials at certain distances from the appliance not the required clearances. For clearances you need to comply with the stove manufacturers instructions and they should have done a temperature safety test to determine minimum distance to combustible material although when I was in the stove designing business EN13240 didn’t require temperatures above the stove to be measured. We did it anyway when we could.Diagram 30, page 42.
The diagram itself doesn't mention clearance above, but the second half of the table below the diagram lists the height above the appliance to non combustible material.
If you have a wooden beam above, then it all becomes more troubled, as you probably wont have the clearance from the flue itself either. This can be gotten around by using twin wall insulated flue, which lowers the clearance to, IIRC, 50mm. But, again, this is flue stuff, not height above appliance (and it was height above appliance that you were asking about, and that is detailed on pg 42)
I think you’re misreading the table on pg42. It states the minimum thickness of non combustible materials at certain distances from the appliance not the required clearances. For clearances you need to comply with the stove manufacturers instructions and they should have done a temperature safety test to determine minimum distance to combustible material although when I was in the stove designing business EN13240 didn’t require temperatures above the stove to be measured. We did it anyway when we could.
Have a read of the whole page including the title at the top of the diagram. The table is telling you the minimum thickness of non combustible walls dependant on their distance from the appliance/hearth and whether or not the hearth butts up to the wall.I think, more likely, we are both wrong, now that I've looked at the table again.
Its not exactly minimum thicknesses of materials, as figures like 1200mm are mentioned and 300mm...
I think that, what its saying is that you need to bring non combustibles up to a height of 1200 above the hearth surface, and to at least 300mm above the appliance.
Im sure its in the document somewhere though - it has the clearance at the sides of the appliance, and to the rear of the appliance (not that i can find either right now) so you would imagine it would have the clearence above the appliance also.
But, yes, you are entirely right - i think i mis read the page that i linked to. Thank you.
Have a read of the whole page including the title at the top of the diagram. The table is telling you the minimum thickness of non combustible walls dependant on their distance from the appliance/hearth and whether or not the hearth butts up to the wall.
No try interpreting it this way (first line of the table) -The minimum height given above the appliance is 300mm, regardless of thickness.
From that, i might infer, that the minimum height, above the appliance, is 300mm, regardless of thickness.
Would you agree?
Do yourself a favour and read the instruction manual for the stove you’ve bought. The manufacturers instructions pretty much override anything else.My head hurts , have bought the stove , an Esse Montrose, it has a removable baffle for sweeping the flue, on our way home we stopped at a pub , (The Earl of Chatham) in Lostwithiel, it has a wood burner fitted ,the gap over the top of the stove was about 4 inches to the closure , ours will have about 8 inches , about 4 inches to the sides and now the gap behind is worrying me , also the stove is in the car and being 71 and vertically challenged that's where it's staying for a day or two , my head hurts even more now , administering alcohol until I no longer care, I like waddycalls post but it makes me want alcohol even more ,
Chris