wolfweld 135 turbo problem

  1. wingnut Member

    Messages:
    27
    Location:
    caithness
    Hi I am new to this forum. So I am sorry if I have posted in the wrong please.the problem I am having is that my wolfweld 135 turbo keeps popping my rcd in my fuse box.it was just plugged into the socket in the wall with a 13amp fuse.so I thought if I put it on it's own circuit I would not have the same problem. So iv got it on it's own circuit with a 16amp rcd and wire it to a blue plug but still having the same problem. Can any help me with this problem or tell me whats wrong?cheers
     
  2. mike 109444

    mike 109444 Member

    Messages:
    4,087
    uk Bristol
    Welcome wingnut. Does it trip as soon as it's turned on or only when the trigger is pressed or when you strike the arc ? Knowing when it trips will allow further diagnosis.
     
  3. wingnut Member

    Messages:
    27
    Location:
    caithness
    When I press the trigger
     
  4. rtbcomp

    rtbcomp Moderator Staff Member

    Messages:
    18,615
    Location:
    Sheffield UK
    Do you mean MCB? An RCD trips on earth faults and is rated typically at 30mA and 30mS, an MCB trips on current and is rated in amps and a letter designating haow fast it trips.
     
  5. mike 109444

    mike 109444 Member

    Messages:
    4,087
    uk Bristol
    But not actually striking the arc (wire on to job) ?
     
  6. wingnut Member

    Messages:
    27
    Location:
    caithness
    Its doing It on both now trigger and arc.sorry its the mcb thats tripping
     
  7. mike 109444

    mike 109444 Member

    Messages:
    4,087
    uk Bristol
    Is the machine a recent purchase (still under warranty) ? Looking back through the Wolfweld section could not see a good clear pic of the inside of one of these machines so difficult to point to something that could be causing it.
     
  8. rtbcomp

    rtbcomp Moderator Staff Member

    Messages:
    18,615
    Location:
    Sheffield UK
    I've moved this to the "Wolf" section.

    The MCB has to allow the current surge through without tripping, what rating letter is stamped on it. Post a photo if you're not sure.
     
  9. wingnut Member

    Messages:
    27
    Location:
    caithness
    16amp
     
  10. rtbcomp

    rtbcomp Moderator Staff Member

    Messages:
    18,615
    Location:
    Sheffield UK
    A, B, C or D?
     
  11. wingnut Member

    Messages:
    27
    Location:
    caithness
    Sorry mate what do u mean? I was just back at the welder.its only tripping on setting 5 and 6.
     
  12. rtbcomp

    rtbcomp Moderator Staff Member

    Messages:
    18,615
    Location:
    Sheffield UK
  13. mike 109444

    mike 109444 Member

    Messages:
    4,087
    uk Bristol
  14. wingnut Member

    Messages:
    27
    Location:
    caithness
    Il get ma spark mate to look at it tomorrow
     
  15. joejoe Member

    Messages:
    26
    UK. North East
    What was the outcome?

    It may be useful to others in the future.


    Cheers.
     