as per title on sunday power went off at house on investigation found this
Now I KNOW it was tightened and also all terminals where checked a few weeks after, the 23 way CU was fitted 10mths ago, the buzz bar was ok ish and cleaned up ok, any body had this happen with a proteus switch?. coz I am a little concerned and relieved at the outcome.
Now at the time of the outage we were not drawing heavily, ie was late ish on, Us two out at concert, lads in bedroom playing games, tumbler, immersion, compressor, all on auto, and a few lights on, Gas central heating, maybe a few things might have switched together, but a few mths ago I was welding heavily for hours with all those on also with no probs
I replaced with a wylex one for the night and was fine, till I could get a replacement proteus but I have managed to get an older style one, that seemed better with slightly larger screw head.
oh BTW have 100A wylex main switch on meter tails before the CU and that is fine.
Now I KNOW it was tightened and also all terminals where checked a few weeks after, the 23 way CU was fitted 10mths ago, the buzz bar was ok ish and cleaned up ok, any body had this happen with a proteus switch?. coz I am a little concerned and relieved at the outcome.
Now at the time of the outage we were not drawing heavily, ie was late ish on, Us two out at concert, lads in bedroom playing games, tumbler, immersion, compressor, all on auto, and a few lights on, Gas central heating, maybe a few things might have switched together, but a few mths ago I was welding heavily for hours with all those on also with no probs
I replaced with a wylex one for the night and was fine, till I could get a replacement proteus but I have managed to get an older style one, that seemed better with slightly larger screw head.
oh BTW have 100A wylex main switch on meter tails before the CU and that is fine.