I am doing some work in an old barn and it has had 3 ph brought in with a new sub main metal CU, with an mcb,s then split down with a 1ph radial and IIRC they have used 6mm (Could be 10mm ) 4 core swa for 3ph and neutral run to the plastic 4 pole rotary isolator, that I am connecting to, but the sparky has used only the swa's armour with standard glands as the earth from the CU, I know this was the old way but thought it had been outlawed and should have a separate earth conductor ie usually 5 core cable.
I called in today to get a 16 a 5 pin switched socket from wholesalers and asked several electricians and was shocked that NO-ONE could answer the question??
Also he has used modern coloured cable so it was bought in to do that job !!