Glad you've got the juice flowing, #6011
look forward to hearing how the full blown test goes!
As PTvor says, the greatest inrush of current is when the arc is struck. If the welder is on a dedicated circuit then you could consider changing the MCB from a B type (e.g. B16) to a C type (C16). B types trip between 3-5 x max current and C types trip between 5-10 x max current.
I'd caution against switching to a C type if it's not on a dedicated circuit (i.e. you have other run-of-the-mill devices plugged in to the same circuit) as there is a reason that B type MCBs are fitted for these.
look forward to hearing how the full blown test goes!As PTvor says, the greatest inrush of current is when the arc is struck. If the welder is on a dedicated circuit then you could consider changing the MCB from a B type (e.g. B16) to a C type (C16). B types trip between 3-5 x max current and C types trip between 5-10 x max current.