I have a number of single phase machines (180 amp Oxford arc welder, 180amp mig and plasma cutter Cut40) that really need a 16 or 32 amp supply. The Mig and Plasma are currently on 13amp plugs.
I have a number of three phase sockets around the shed but the single phase is just normal 13 amp.
Can I run 16/32 amp plugs from one phase of the three phase sockets with an adaptor lead or are there reasons not to so this? I have some spare points at the distribution board so could get dedicated supplies put in but of i can avoid that it would make things quicker!
I have a number of three phase sockets around the shed but the single phase is just normal 13 amp.
Can I run 16/32 amp plugs from one phase of the three phase sockets with an adaptor lead or are there reasons not to so this? I have some spare points at the distribution board so could get dedicated supplies put in but of i can avoid that it would make things quicker!


if that was the case and you have a 3 phase board with mixed 3 phase and single phase breakers the main rcd would not stop on
rcd work on current imbalance so if you take off one of the phases and use the neutral the load is balanced