It will work fine but, if you break one of the switch lines it will still be at a voltage on one side of the break with possibly not a low enough impedance to Earth to trip the breaker due to the coil of the contactor being still in the circuit but still enough power to kill you.
Also an earth fault on certain parts of the control circuit would energise the contactor and start the machine.
I just said it doesn’t comply with UK wiring regs as the neutral is switched.
Schneider supply all over the world so it may be difficult for them to show a diagram that complied with everyones regulations and it might just be that it’s easier to wire it this way due to terminal locations.
This scenario could still happen if it were wired with the phase and neutral of the control circuit wired to comply with UK regs (swapped) if there was a break in the neutral.
But there is less neutral wiring to go wrong adding an extra bit of safety.
Also an earth fault on certain parts of the control circuit would energise the contactor and start the machine.
I just said it doesn’t comply with UK wiring regs as the neutral is switched.
Schneider supply all over the world so it may be difficult for them to show a diagram that complied with everyones regulations and it might just be that it’s easier to wire it this way due to terminal locations.
This scenario could still happen if it were wired with the phase and neutral of the control circuit wired to comply with UK regs (swapped) if there was a break in the neutral.
But there is less neutral wiring to go wrong adding an extra bit of safety.