Lovely job, the next drill I get will be the sameNearly done.
View attachment 410187
Just got the quill handles to make, knobs to hold the lid down to adapt and fit and wire up the VFD.
View attachment 410188
VFD just arrived so I'll test that tomorrow.
It seems to be the drill/VFD and only when it is idle
Almost all modern motors have the junction box up near the shaft end. So would clash with the cover.
With your edit, I think you have realised the weakness in the link you make between effect (RCD tripping) and cause.
If the VFD is switched on but is idle (i.e. its output is zero), you should be able to dead short the three phases and nothing happen.
If, when its output is low, anything at all is coming out of the VFD, then that would point to a VFD fault.
Even so, you should even be able to switch the VFD output high with the phases shorted and the VFD should fault out without the RCD tripping.
@brewdexta I had a problem with ABB VFDs tripping the breaker too.
Made a small post about it today.
Maybe try a similar filter I installed on all of my ABB VFDs/disable the internal EMC filter if you can on your VFD.
I hope it works for you. RCDs/RCCBs do not like interference which causes nuisance tripping.I've had a chat with my spark, he recommends I get a type A 30mA trip RCD. If I go for the 100mA trip then my workshop sockets will be out of spec as its got to be 30mA. So we will give that a go first, if that fails then we may put a separate supply into the workshop for VFDs only, a bit of a pain but every day is a school day.
I forgot to add that we found the culprit. Once we moved circuits onto individual RCBOs, only one was tripping intermittently, that was the one with pellet boiler on. It appears that the igniter on the pellet boiler was on its way out. I swapped that out and it all stopped, so it must have had a bit of earth leakage and the VFDs exacerbated the issue making the RCD trip sporadically. I now have 3 VFDs on the same RCBO with no issues.The spark came, changed out the RCD for an A type, had a cup of tea and about 10 mins after turning the VFD on, it tripped the RCD.
The spark's opinion is that there are quite a few MCBs for various circuits on that RCD and there is probably an amount of leakage already, and the VFD is just tipping it over the edge. So we turned them all off except the workshop ring, left it for half an hour, and nothing tripped. he could have started to measure stuff but I think this is good enough. Its been an hour and nothing has tripped.
So, the plan is to swap out the old plastic split load consumer unit for a new metal one with RCBO for each circuit. Its something I wanted done anyway, its just accelerated it. While he's doing that, he's going to put in a couple more 3 phase sockets for me for the machines I don't want speed control on.