Has anyone else had issues with Honeywell tank stat calibration being out?
Specifically these - https://www.screwfix.com/p/honeywell-home-l641a-cylinder-stat/40051
We have three on our newly installed thermal store to control various pumps and the boiler and none seem to correspond with the expected readings across the tank. I.e. the lower one controlling the boiler is about 4inches lower than one comtrolling a pump circulating the central heating. The lower one clicks at about 55C when the one 4 inches higher clicks at 50C. No way should it be hotter lower down.
Are there more reliable brands? I thought Honeywell made decent stuff but they just dont seem right.
Specifically these - https://www.screwfix.com/p/honeywell-home-l641a-cylinder-stat/40051
We have three on our newly installed thermal store to control various pumps and the boiler and none seem to correspond with the expected readings across the tank. I.e. the lower one controlling the boiler is about 4inches lower than one comtrolling a pump circulating the central heating. The lower one clicks at about 55C when the one 4 inches higher clicks at 50C. No way should it be hotter lower down.
Are there more reliable brands? I thought Honeywell made decent stuff but they just dont seem right.




.
. We contemplated a leak rad on the system and can add one later if needed but decided not to and to get the heat into the store and around the house instead. Its not much of a risk when we are out as its always left topped up and damped down on tickover as no point having it racing if we are out so nothing will get too hot then. Eventually i want a generator setup to run the boiler and pumps in a powercut. I know where the supply for the lot is so this would be fairly easy to rig up.