is the 4mm swa running from house to garage?
Just wondering as i would protect that with 20A mcb, I would say 32A for 6mmsq ,45A for 10mmsq and 63A for 16mmsq.
I've got in my table...
38A max,
11mV /A /m volt drop so for 10mtr @ 30A..
11mV x 30A = 330mV/m
10m x 330mV = 3300mV or 3.3v drop.
of course i may be up the spout but thats how i read it:-)
Dave
They are for
"Armoured multicore pvc insulated cable to BS6346",
"One or two core cable",
"single phase AC",
"open, clipped direct or on non-metallic surface installation"
Dave
Dave, it was my original post and I still haven't found the answer to my question about burial or fence clippage. Where did 30A come from? According to TLC's voltage drop calculator;
SWA (3 core) XLPE
Load 12 kW
Voltage 230
Length of Cabling 70 metres
Required Cable Size 16mm
Voltage Drop 9.1volts.
Percentage Drop 4%.
Load = 52.17amps.
Ah, now that's what I thought! I think the sparky who's going to do the work has read into that that cables MUST be buried 600mm deep. Where did you 'glean' that info from please?