An oxygen cylinder glowing red hot in 2 seconds doesn't make sense. There would have to be a "perfect storm" of a combination of factors, such as a nearly empty cylinder (internal pressure less than acetylene cylinder pressure), and a torch tip blockage, causing acetylene to flow back in into the oxygen cylinder, combined with operator error in failing to check for gas flow out of the nozzle.Was talking to somebody years ago, no flashbacks, torch went #puff. He turned around, oxygen cylinder glowing red hot in two seconds
the hoses are a good branded one and been on 25 years in nice condition. the gear gets used about 8 times a year but i wouldnt be without it . i hear these horror storys all the time from people who have never even used itThere will be someone on here who has used O/A for 50 years with neither non-return valves nor flashback arrestors - with no bother.
If a flashback arrestor is effective, you should not really need two in series but these days, there is very often a flashback arrestor at both ends. The one on the torch is also a non-return valve.
The flashback arrestor at the torch probably stops the 50 year old hose from bursting and causing a fire.
CIGWELD Comet Flashback Arrestor – Oxy-Fuel Set – Torch End | BOC Gas
These COMET™ FBA’s are designed to prevent flashback flame and reverse flowing gases inside the regulator or blowpipe from burning or mixing in the hose and gas supply system.www.boc.com.au
Jack
They are there to prevent a flashback getting to the cylinders so that is where they go. Waste of time having a set at the torch end.I suppose there is the extra weight on the torch, especially for light brazing setup (why I have asked).
2 makes all the sense in the world, too.
Torch end I'd say is the best for first line defence, so mine are staying there. Double protection from crappy hoses, then cylinder end, Hmm.
YEP just the one way check valves on torch to stop the gas mixing in the hoses .the only time flashbacks are fitted on both ends is if the hoses are longThey are there to prevent a flashback getting to the cylinders so that is where they go. Waste of time having a set at the torch end.
If you were doing a risk analysis, you would likely set the probably of failure quite low, but the consequences of failure at catastrophic. The weighted risk is then significant.the hoses are a good branded one and been on 25 years in nice condition. the gear gets used about 8 times a year but i wouldnt be without it . i hear these horror storys all the time from people who have never even used it![]()
As I mentioned, they also protect the hoses. Here is an excerpt from a standard published 25 years ago.
AS 4839—2001
7.3.3 Flashback arrestors at both hose ends (optimum protection)
Optimum protection is provided when at the blowpipe end a flame arrestor and a non-return valve for each gas line is fitted, and at the regulator end a flame arrestor, a non-return valve and a temperature activated cut-off valve for each line is fitted. Pressure activated cut-off valves at the regulator end are optional. The options in Clauses 7.3.4 and 7.3.5 below provide lower levels of protection and should be used only when it is not otherwise possible to achieve the rated flows of the end heat output device through the lack of outlet pressure from the pressure regulator.
7.3.4 Flashback arrestors at the blowpipe hose ends only
A flame arrestor and a non-return valve shall be fitted to each blowpipe inlet connection.
7.3.5 Flashback arrestors at the regulator hose ends and check valves at the blowpipe ends
At the blowpipe end, non-return valves shall be fitted on each gas line. At the regulator end, a flame arrestor, non-return valve and a temperature activated cut-off valve shall be fitted to each gas line. A pressure activated cut-off valve may also be fitted at the regulator end of each gas line.
Note that there is not a clause that lists "protection" at the regulator only. Where flashback arrestors are only listed for fitment at the regulator, non-return valves are fitted at the torch.
Such standards legally apply to industry, not a backyarder, but that doesn't make them a "waste of time".
Jack
You are quoting an Australian standard.
I was trained using British standards. If you have only one set of flame arrestors they must be fitted at the regulator end. The main danger of a flashback is from the gas bottles.
If the hoses get cut and you have the arrestors fitted at the torch end the bottles no longer have any protection.
I've been using and testing oxy fuel equipment for many years and I've yet to see 2 sets of arrestors fitted.
The standard setup is arrestors at the tanks and non return valves at the torch end of the hoses.
If the hoses get cut, how will anything flow backwards ?If the hoses get cut and you have the arrestors fitted at the torch end the bottles no longer have any protection.
A leak at the regulator would be to free air or "atmosphere" ?A leak at the regulator or hoses wrapped up and placed on the bottles.
Acetylene is dissolved and stored at really low pressure.
If it's full there is less chance of a problem but as the bottle empties and the pressure drops even further the chance of the flame popping into the bottle increases and then the **** really hits the fan.
If the hoses catch fire there is the possibility of a flashback.Just as a matter of interest, if the hose is cut, arrestors at the regulator will not help, even if there were the possibility of a flashback.
Normally - they will cut off the gas if there is a flashback or over temperature, but not if the hose is cut.
Jack