What's different about an EV charge point that a normal MFT can't test?You’ll also need an EVSE adapter for your MFT to carry out the required install tests.
What's different about an EV charge point that a normal MFT can't test?You’ll also need an EVSE adapter for your MFT to carry out the required install tests.
Use really really strong string in the duct….nothing more annoying than a big cable and a snapped stringAll great points thanks. I know loads more than I did 24 hours ago. Some measuring to do over the weekend and line up some digging / order some duct.
just wired one up 2 day in 3 core swa and seperate cat 5 cable for the ct clamp , no need for it to go in the db . got another 2 to extend the cables on another job and move the position of the chargersRef the Cat-5, I presume there's no issue running normal SWA then an additional Cat-5?
I'll probably run a 50mm or bigger duct for the SWA with a 20mm inside that for the Cat-5.
Don't like the idea of taking the Cat-5 into the consumer unit tbh, that seems mad. You'd then have to bring it out of the consumer unit via a gland to wherever it then goes.
Use really really strong string in the duct….nothing more annoying than a big cable and a snapped string
What's different about an EV charge point that a normal MFT can't test?
Don’t forget the earth rod if your supply is PME.
Don’t forget to ensure your incoming mains supply is not on a ‘looped’ circuit.
DNO will need to know about any 7kW EV charger being installed.
I wish I did. Its like a foreign language in here.All great points thanks. I know loads more than I did 24 hours ago. Some measuring to do over the weekend and line up some digging / order some duct.
I wish I did. Its like a foreign language in here.
I can usually follow most things but much of this is double Dutch. Not sure if if it's the bottle of Red I treated myself to, or it really is as complicated as it sounds
No wonder my son struggled with his city and guilds exam with no tuition. Lol
What's different about an EV charge point that a normal MFT can't test?
What MetalMonkey says. It simulates the different communication states the car has with the charger and the charger should respond in a certain way and then cut off the power to the car under certain conditions, you're confirming that happens with the adapter.AFAIK The EV adapters you get for the MFTs basically simulate having a car connected to the charger so you can test the outputs of the charger and simulate a fault to check it.
It was due to the risk of a broken neutral on the suppliers side (not as uncommon as you'd hope). In the event of this happening all earthed metal work rises to dangerous voltages which isn't so bad inside your house when you're within the equipotential zone but move things outside where you're stood on the ground, possibly wet ground, and you touch the car body that has risen to a dangerous voltage and you're at zero volts you become the earth path.The reason they are insisting on an earth rod close to the vehicle is, I think, due to the possibility of connecting between phases with another vehicle charging from a different phase, in a similar situation. I think there has been some consternation re street chargers not being sufficiently ground protected?
this is putting the onus onto electrical installers/designers rather than holding the DNOs and there shoddy networks to account.
Just a word of warning about how built in PEN fault protection is usually implemented...the EVSE constantly monitors the line voltage and checks to ensure it's within the statutory requirements, in the UK 230V +10%,-6% (216V to 253V), if it falls outside these limits for more than 5secs (I think) it isolates the power to the vehicle. If done correctly the manufacturer should inset the measurment limits to account for manufacturing tolerances, temperature and drift over lifetime. If your supply is close to the limits then it's possible you'll exhibit false triggering of the protection circuit.