Might just need a new Schrader valve in the vessel. Check it for leaks if you pump it up.
cant pump up as dont think ive got any thing for it
Have you verified the water is being pushed out of the prv?
Fooked heat engines are very common.
Top up boiler, isolate it from the heating circuit via the 2 iso valves on the flow and return under the boiler, leave overnight, if pressure stays put its likely on the rads/pipes.
If it's still loosing water check the condensate to see if water is running down it, that will confirm if the heat engine is porus
thanks for all the help guys i think on this any cheaks that i can do from under neath and out side see if water leaking i will do but as for changing parts im not up for as the boiler works as is i dont want to get in a point that it dont work after me having looksee and as needs a service might have the bloke do the both
As kayos has stated pressure vessel my re pressurise.
You can rule out pressure vessel by draining one of the rads to create an air pocket as temp fix, prvs very often continue to dribble though as once they open on an old boiler they don't like to re seal crud etc.
External expansion tank can be fitted should cost you very little for a 10Ltr a flexi and a pushfit tee, as long as you have somewhere for it to live.
and sounding like i might not want to touch this all info will make sure they dont get riped off i have a few plumbers that i can call but better for warned rather than take what they say as the bible but have used them for a time and they do seam good and fair