Thanks, it does. I had this checked when I fitted the C curve for the ramp (might have been you that suggested it then). Just want to be sure whether I need the C for the TIG.What you really need to ask is whether your installation will still meet the earth fault disconnection times if you fit a C curve breaker, a local sparky can advise.
they only trip when the current rating exceeds 10 to 20 times the rated current of the breaker, so a 16 amp d type mcb trips at about 320 amp
most gear with a high starting current only need a c type max