My Miller not only runs the three voltages you listed but does anything between 115v-460v,You can change to either 415v, 240v, 110v. Looks pretty damn versatile. Usually only the newer Miller or Lincoln, machines can do that, and then its either 415v and 240, or 240v or 110v, rarely all three.
Would make sense if it was for that reason.My Miller not only runs the three voltages you listed but does anything between 115v-460v,
i'm guessing to make the one machine more sellable worldwide?
I take it those ratings are for plain PVC rather than XLPE? Was gonna go for 16mm XLPE as it's rated at 110A. Supply fuse is luckily enough 100A.i'll get a weight and get you a postage cost, plus say couple of notes for the jiffy poke, I bought it, though ended up using small switchfuse instead (my meter tails are 6 metres long, suppliers tend to want switchfuses on anything beyond 3 metres to protect their cutout fuses) (technically its illegal to pull a cutout fuse if your not an employee of the DNO - SSE/Scottish Power/ManWeb etc etc, but many do, if you ever decide to (not that im condoning it *whistles*) turn the main switch off at the CU, otherwise there will be a load present and you risk arc burns / death / causing a major short and blowing the pole transformer cutout thus making you highly unpopular with the neighbours :P)
10mm2 is good for ~64amps, 16mm2 ~80Amps, 25mm2 ~100amps or slightly more. If you have a 100amp supply but run smaller SWA to the shed, it MUST be fused down to protect the SWA from becoming overloaded. (Finding out what supply fuse size you have is *fun* suppliers often don't have a clue...more often than not, they send someone out to have a look....
Basically PME lowers your earth impedance big style (supplier bangs rods in here there and everywhere) plus with TT, you can't rely on the earth impedance being constant (soil moisture levels being a big part, long dry summer (yes those rare ones we get) can cause the soil to dry out, dry soil doesn't conduct and so your earth impedance goes all to heck) so instead of relying on MCBs to Automatically Disconnect Supply (ADS) for fault protection, you then rely on an RCD for fault protection.
Also if there is a fault on a neighbouring property, its not uncommon to get a "tingle" or worse off earthed metal work in your place as the fault tries to find a path back to the transformer. (fault current doesn't flow to earth, rather it flows through the earth back to the transformer)
Oddly the ex shooting lodge I quoted on (got passed over for someone else..win some lose some) had a 3 phase incomer, but 2 single phase recent meters...even SSE had no idea why a 3 phase meter hadn't been fitted...especially as the standing charge on a 3 phase meter is the same as a single phase meter, so the previous owner was paying double for no reason...though the electrics dated back to the 1940s....
I really hate the way part P has been misused as a means to discourage the amateur electrician; most of it is donkey work, the bits that really justify a pro are few, at least in the domestic environment.Very nice buy, eschen. Apologies for coming over all Mr. Regulations, but the new circuit to the shed will be notifiable which effectively means it's got to be designed, installed and tested by a spark.
I paid £800 all in for 50m of SWA, a garage CU, 13A sockets, lighting and a 32A socket in the garage.
I really hate the way part P has been misused as a means to discourage the amateur electrician; most of it is donkey work, the bits that really justify a pro are few, at least in the domestic environment.
I bloody hate making off SWA. Got to do one later today - again, madness that I'm competent to do electrics at work, but can't at home![]()
I have a kew technik BladeRunner, which is OK, but it's still a pain I find to make the gland off. Is the armourslice any better?Have you tried the CK Armourslice works a treat.
I have a kew technik BladeRunner, which is OK, but it's still a pain I find to make the gland off. Is the armourslice any better?