Ok so sizing the boiler is fairly simple calc (volume of rooms, insulation, windows, room type, local weather conditions plus some, temp needed) but how do I size the thermal store so I can do one burn (with refills if needed during the evening so that in the morning it will release enough heat to warm the house back up?
The more I look the more questions seem to apear.
Justme
you'll need a certain amount of power for heating, say 8kW continuously
let's say your stove does 24kW so you can store 16kW's of it... you can than have it going 33% of the time...
33% of the time you will have to have the fire going, let's say you do this 8hrs a day to heat the house for 24hrs..
you'll need a buffer of 16kW*8hrs=128kWh's
now you will have to decide for you buffer temperature which is depending on the feed temperature.. let's say 70 degrees here and let's say 40 degrees when it's empty
you'll have 30degrees temperature difference to store heat in..
given E=M*C*T1-T2
M=E/(C*dT)
where E=energy=128KWh=128*3600=460800kJ
M=mass
C=specific heat: 4,2 kJ/degree*kg (for water)
so M=(128*3600)/(4,2*30)= 3 657kg's of water so around 3 cubic meters
you could include heat loss in this, but since your storage is likely to be in your basement or at least in the house, the lost heat will be added to the house...
change the values above to realistic values for your situation..