MattH
Member
- Messages
- 4,524
- Location
- Cornwall
I've just added 6 new 4ft twin battens fittings to a lighting circuit.
The circuit already had 5 4ft twin fittings.
The fittings have twin 18w LED tubes and starters in them. All fed with 1.5mm T&E from a 6A B type MCB.
So 11 fittings total, with 22 x 18w 4ft tubes totaling 396 Watts, with power factor of 1.8 that's still less than 2A (about 20M total to last fitting).
Problem is that when all fittings are connected after about 5 mins the MCB trips.
If I disconnect any 1 fitting the MCB stays connected.
Any ideas? Even if I take the full load of the ballasts (non HF type) into account then it's still less than 4A with power factor applied.
The circuit already had 5 4ft twin fittings.
The fittings have twin 18w LED tubes and starters in them. All fed with 1.5mm T&E from a 6A B type MCB.
So 11 fittings total, with 22 x 18w 4ft tubes totaling 396 Watts, with power factor of 1.8 that's still less than 2A (about 20M total to last fitting).
Problem is that when all fittings are connected after about 5 mins the MCB trips.
If I disconnect any 1 fitting the MCB stays connected.
Any ideas? Even if I take the full load of the ballasts (non HF type) into account then it's still less than 4A with power factor applied.