Possibly have the opportunity for a larger plasma cutter which requires a 32a supply.
This is my current install. Would it be simply enough to add a socket in garage? Want some idea before I get an electrician in.
House consumer unit. Garage is 40a on the right
Garage consumer, have a couple 16a sockets, one of which can go as no longer required
This is the cable linking the two Believe it is 10mm
This is my current install. Would it be simply enough to add a socket in garage? Want some idea before I get an electrician in.
House consumer unit. Garage is 40a on the right
Garage consumer, have a couple 16a sockets, one of which can go as no longer required
This is the cable linking the two Believe it is 10mm

just fit the socket and a 32 a breaker . the only time I have seen a problem with cable getting warm is on a 10kw shower on 10mm cable . that is a constant full load and it was in insulation in wall and attic its not going to happen on your set up