Has anybody successfully powered a 3 phase input VFD from a single phase supply by de-rating the drive?
The situation is as follows:
1. I need to power a 3 phase - 230v - 3kw motor (wired in Delta).
2. I only have single phase supply available.
3. I have got an ABB ACS 355-03E-15A6-4 (7.5kw) VFD. It has been designed for three phase power input.
I have read on a few sources that a 3 phase 'only' input VFD can in theory be powered by a single phase supply but the drive/VFD needs to be de-rated by a minimum of 50%.
In theory my 7.5kw ABB VFD will then become a 3.75kw VFD, enough to power the 3 phase 230v 3kw motor (3.75kw will obviously be too much for a 3 pin, 13A plug so I will wire the supply direct from a MCB with the appropriate thickness cable).
There is some VERY limited information here.
Has anybody successfuly de-rated a 3 phase input VFD so it can be run on single phase?
Specifically interested to know if it has been done on an ABB ACS355 drive.
The situation is as follows:
1. I need to power a 3 phase - 230v - 3kw motor (wired in Delta).
2. I only have single phase supply available.
3. I have got an ABB ACS 355-03E-15A6-4 (7.5kw) VFD. It has been designed for three phase power input.
I have read on a few sources that a 3 phase 'only' input VFD can in theory be powered by a single phase supply but the drive/VFD needs to be de-rated by a minimum of 50%.
In theory my 7.5kw ABB VFD will then become a 3.75kw VFD, enough to power the 3 phase 230v 3kw motor (3.75kw will obviously be too much for a 3 pin, 13A plug so I will wire the supply direct from a MCB with the appropriate thickness cable).
There is some VERY limited information here.
Has anybody successfuly de-rated a 3 phase input VFD so it can be run on single phase?
Specifically interested to know if it has been done on an ABB ACS355 drive.