We have a 3.7Kw array and our record for a 24hr period is 27Kwh.
Fixed that for you.
48v nicad system (68v absorb set point). We were in float by 1pm iirc. .
Thanks for that, I'm still reeling a bit from all the good info from the members.Bimble Solar is the place to get cheap panels.
Let me guess, inverter came cheap and determined system voltage? 48v is nicesmall breakers, smaller wires
Mechman, just some info for you. Solar panels have an open circuit voltage (with no load connected) and a voltage at which they produce the most power (like the volt/amp curve of a welder). This voltage is called the maximum power point.
A decent (maximum power point tracking) charge controller will attempt to load the solar panels up so the voltage drops to the maximum power point, so you get the most power (watts) from the panels. The charge controller then lowers this voltage to charge the batteries. You see in my picture, the peak panel voltage was 127v, the peak current was 30.4 amps and the maximum power was 1.91kw.
There was a lot of sun that day so we made 5.1kwhr (units) of electric.
Looking at updating to a 48v unit & dropping 6 cells off the battery. Will be looking for new cells in the next year or two as well.
Selling the old inverter charger, 6 cells & outback FM80 would pay for the new inverter (or poss two, three would be nice to get 3 phase but would want it re-configurable to all single phase too) which will also do the solar.