Hi Guys,
I have just had an electrician come in to put in the wiring for a Clarke 4hp 3kW compressor. I don't have the compressor yet so I can't test that the wiring is correct.
I have had a dedicated line run for the compressor and the electrician has put in a 40amp type B breaker, with a 6mm2 SWA cable and a 32amp blue commando socket & isolator switch unit.
Does this sound all ok? I think at 3kw the compressor draws around 12amps at full power, so the 32amp socket and isolator will be fine. Will the cable be okay? Will the type b breaker be ok with the starting surge? Clarke recommend 40 amp wiring.
Many Thanks
Many Thanks
at most the b type breaker might need changing to a c type if it trips on start up its no big deal. half the jobs i go to wiring for machines u only get the spec from the supplier and the firm conect up to what u have wired