Hello Georgie,
I was questioning the post by Wheresmejumper saying a double 13 amp socket is meant to carry less than 26 amps combined. The rating of the circuit breaker be it RCD protected or not is dependant on the circuit, if it's only rated at 15 amps then clearly you can't fully load a 13 a twin socket but on a 32 a circuit you can.
Talking about 11 Kv, I saw the aftermath of a situation where a breaker feeding a pump wouldn't trip and they needed to stop this pump. The rather crazy solution was to rack the breaker out, what a mess that made, melted the breaker and the spouts. But as it was underground I guess they couldn't just open the incomer to the bars.
Alec
I was questioning the post by Wheresmejumper saying a double 13 amp socket is meant to carry less than 26 amps combined. The rating of the circuit breaker be it RCD protected or not is dependant on the circuit, if it's only rated at 15 amps then clearly you can't fully load a 13 a twin socket but on a 32 a circuit you can.
Talking about 11 Kv, I saw the aftermath of a situation where a breaker feeding a pump wouldn't trip and they needed to stop this pump. The rather crazy solution was to rack the breaker out, what a mess that made, melted the breaker and the spouts. But as it was underground I guess they couldn't just open the incomer to the bars.