Distance from house CU to where the wall charger is around 30 metres, I’ve had a look at a cable size calculator and it seems to show that a 6mm SWA is fine, cable running under solum and clipped externally.
The charger I’m going to get is a Hypervolt, their installation manual says that for longer runs 10mm is preferred, it also says a CT clamp is necessary so presumably that means 3 core plus a data cable all within the SWA, It also states a dedicated CU with 40 amp double pole RCBO which I’ll get as I don’t have any spare ways otherwise, the CU in my house which supplies the workshop has a spare 40 amp MCD but from what I’ve researched this is not correct for the job and this CU already has a 10mm SWA going to it and doesn’t leave much room for another.
So 32 Amps, 30 metres, what’s acceptable 6mm, clearly 10mm would be preferable but I don’t want to spend more than is necessary.
The charger I’m going to get is a Hypervolt, their installation manual says that for longer runs 10mm is preferred, it also says a CT clamp is necessary so presumably that means 3 core plus a data cable all within the SWA, It also states a dedicated CU with 40 amp double pole RCBO which I’ll get as I don’t have any spare ways otherwise, the CU in my house which supplies the workshop has a spare 40 amp MCD but from what I’ve researched this is not correct for the job and this CU already has a 10mm SWA going to it and doesn’t leave much room for another.
So 32 Amps, 30 metres, what’s acceptable 6mm, clearly 10mm would be preferable but I don’t want to spend more than is necessary.