If you're installing a 16A socket the breaker should really be 16A, not 20A.Good point. I actually have a spare 20a circuit reserved for garden socket, but I'd need to install a 16a socket first. What plug do these things come with?
If you're installing a 16A socket the breaker should really be 16A, not 20A.Good point. I actually have a spare 20a circuit reserved for garden socket, but I'd need to install a 16a socket first. What plug do these things come with?
You are going g to need to drop that 20a breaker out and replace with a 16 as well...Good point. I actually have a spare 20a circuit reserved for garden socket, but I'd need to install a 16a socket first. What plug do these things come with?
If you're installing a 16A socket the breaker should really be 16A, not 20A.
While I dont disagree with this advice at all, most small inverter sets will quite happily run a 3.25 rod from a 13amp plug. Mine does it quite happily at the end of a 30m extension lead.You are going g to need to drop that 20a breaker out and replace with a 16 as well...
I can run my 200amp tig flat out on a 13amp plug, and my mig...but if he wants a 16 amp socket then a 20a breaker is an issueWhile I dont disagree with this advice at all, most small inverter sets will quite happily run a 3.25 rod from a 13amp plug. Mine does it quite happily at the end of a 30m extension lead.
Maybe show us some sketches of what you are proposing and then we may or may not be able to guide you further.