I'm installing a 2kw under sink 10 litre water heater. It is 3m from the fuse box, fed with 1.5mm2 3 core pvc flex inside some mini trunking.
My calculations say that it should draw under 9 amps full loads, would a 10a type B MCB be enough to feed it? The other choice I have is a 20a type B, which I think is too high. I think I already know the answer - a 16a type B but I just want to check with the proper sparkies. Unfortunately I don't have a 16a in my spares box so I would actually have to buy one!
My calculations say that it should draw under 9 amps full loads, would a 10a type B MCB be enough to feed it? The other choice I have is a 20a type B, which I think is too high. I think I already know the answer - a 16a type B but I just want to check with the proper sparkies. Unfortunately I don't have a 16a in my spares box so I would actually have to buy one!