Right i'll be rebuilding my shed/carport into a garage/workshop shortly. I'm aware of Part P and all that guff so we don't need to get into that this is purely a circuit design question.
The shed curently has power run to it wired from the house CU on a 40amp breaker it's run by some chunky T+E through some plastic tubing buried in the ground but i'm going to replace that with some proper SWA. I believe 3 core 4mm will be sufficient for my needs out there. (rated at 42 Amps according to http://www.tlc-direct.co.uk/Products/SW4slash3.html)
The bit i could do with some advice is regarding the circuit ratings. I've currently got a 2 way CU in the shed again witha 40amp main RCD??(can never remember the right acronym) then a 16 amp MCB for sockets and a 6amp MCB for lighting.
I'm running a compressor, a welder (Clarke 160) and various power tools. On occasions the compressor will cause the 16 amp circuit to trip if other stuff is on at the same time when it tries to fire up.
I'm thinking i should prehaps fit a new CU (4way) in the workshop with a dedicated 16amp/32amp? circuit for the welder, another 16amp/32amp for the compressor and then the rest of the wall sockets on a 16amp breaker and the lights again on a 6amp.
I was going to fit 2x16amp wall sockets 1 for the welder and 1 for the compressor and replace their current 13amp plugs with the blue 16amp jobbies.
What do you reckon??
Cheers
The shed curently has power run to it wired from the house CU on a 40amp breaker it's run by some chunky T+E through some plastic tubing buried in the ground but i'm going to replace that with some proper SWA. I believe 3 core 4mm will be sufficient for my needs out there. (rated at 42 Amps according to http://www.tlc-direct.co.uk/Products/SW4slash3.html)
The bit i could do with some advice is regarding the circuit ratings. I've currently got a 2 way CU in the shed again witha 40amp main RCD??(can never remember the right acronym) then a 16 amp MCB for sockets and a 6amp MCB for lighting.
I'm running a compressor, a welder (Clarke 160) and various power tools. On occasions the compressor will cause the 16 amp circuit to trip if other stuff is on at the same time when it tries to fire up.
I'm thinking i should prehaps fit a new CU (4way) in the workshop with a dedicated 16amp/32amp? circuit for the welder, another 16amp/32amp for the compressor and then the rest of the wall sockets on a 16amp breaker and the lights again on a 6amp.
I was going to fit 2x16amp wall sockets 1 for the welder and 1 for the compressor and replace their current 13amp plugs with the blue 16amp jobbies.
What do you reckon??
Cheers