to hire one for a week is £200 so might as well buy oneno look up macfarlan generators on google it gives the calculations for start up loadnot a chance as you would require tripple to start the motor

tried it again on that site and it now shows 4kvh for a 2hp that would work the compressor but would it still work the clarke welder?
tried it again on that site and it now shows 4kvh for a 2hp that would work the compressor but would it still work the clarke welder?[/QUOTE]
try again 3hp 4kw i would agree with that it is a minefield with a lot of variablesjust found this web site http://www.sawdustmaking.com/ELECTRIC%20MOTORS/electricmotors.html which says
Capacitor Start
This motor has a capacitor in series with a starting winding and provides more than double the starting torque with one third less starting current than the split phase motor. Because of this improved starting ability, the capacitor start motor is used for loads which are hard to start. It has good efficiency and requires starting currents of approximately five times full load current. The capacitor and starting windings are disconnected from the circuit by an automatic switch when the motor reaches about 75% of its rated full load speed.
Uses
Common uses include: compressors, pumps, machine tools, air conditioners, conveyors, blowers, fans and other hard to start applications.
me and brightspark seem to have differing opinions as to what size genny will start your compressor i suggest you contact a company that sells gennys and ask for their advice as i think it will be a capacitor start motor.
however either me or brightspark could be wrong or both and i would hate you to waste your cash if i am wrong so take some advice from a specialist before buying