Yes, the full load current appear to be 2.9 from the plate so this is what you would set the inverter max current limit to (might be a parameter called imax, i limit, current limit or similar)
Low speed and high speed settings are the min and max speeds you want the inverter to run at. You don't want the low speed so low as to lose cooling, something like 15hz is enough but you can feel the airflow through the motor and judge how low you can go. Too low and you can cook the motor if run for long periods at low speed.
for high speed - generally yes you can run at higher speed than 50 hz but seeing as your already running on reduced voltage then I wouldn't go too far, but there should be no harm in trying as a test. It'll either work or it won't, I would take a guess even with the reduced voltage it would still be ok at higher speeds.
How does the clutch operate, you may need to do some jiggery pokery to get this to work depending on the existing arrangement as the inverter won't supply the existing switchgear. (Unless it's mechanical?)
Brilliant, thanks. Guess what I'm doing tomorrow

The clutch is mechanical.