went out tonight to bodge a jig up for bending threaded rod in to u bolts . plugged the oilcooled in of went the trip
it normally takes the 30 amp mcb out on start up and a quick reset and its fine. having fitted an rcd fusebox 6 month ago its the 1st time ive used the welder and it was the rcd not the breaker
it has a rubber flex feeding it that's been on over 40 years took the top off and the rubber was well perished and the neutral touching the earth .cleaned all the terminals and tested the welder for earth leakage . readings on megger were just under 1 megohm
so alls good . just need a new flex on it now thank god it wasn't the tranny faulty