Anybody see why I cannot ?
What size protection will I need if single phase is possible.
If I'm reading it right (and I'm probably not). If I'm using the full 255amp, I'll be able to use the set for 40% of the time and pull 74 amp out of the supply circuit....not that I'm going to though ?
So for max 150amp, I'll be able to run it 100% and pull only 38amp ?
I'm not going to be welding anything for hours on end at high amps so hopefully I'll be OK?
I've attatched a pic of the rating plate.
Thanks
What size protection will I need if single phase is possible.
If I'm reading it right (and I'm probably not). If I'm using the full 255amp, I'll be able to use the set for 40% of the time and pull 74 amp out of the supply circuit....not that I'm going to though ?
So for max 150amp, I'll be able to run it 100% and pull only 38amp ?
I'm not going to be welding anything for hours on end at high amps so hopefully I'll be OK?
I've attatched a pic of the rating plate.