Hi all,
I know there are a few excellent sparks on here so just looking for a bit of advice. Have recently moved into a new house and the electric shower is terrible, water pressure is good though. I have a plumber coming Wednesday to advise if I could run one from the combi but I fear due to length of hot water run a meagre electric shower upgrade will have to suffice. Currently there a 9.5Kw one in, I would want to bump it to a 10.5Kw, anything would be better.
I've done some research but just looking to clarify to see if the current wiring is suitable, I just want to make sure things are safe.
So 10.5Kw/230V = 45.65A
I have a 10mm2 cable coming from the CU into a standalone 63A RCD, up some plastic trunking into the loft where is it not clipped onto anything then goes into the shower switch then from there down a cavity wall into the shower. The run from the CU to the shower is approx 8 metres.
There was some insulation in the loft on top the cable which can be permanently moved on put under the cable. The ceiling and walls are lath and plaster. I would say there is no insulation in the cavity wall based on the other walls having none but I cannot confirm. Which reference method should I use to determine the cable rating?
It wouldn't be a huge deal to replace the cable with 16mm2, but wouldn't that be hellish to terminate in the switch and shower? FYI I am pretty happy doing a bit of wiring usually but will probably have a spark deal with a shower if that's the way I have to go.
Thanks,
G
I know there are a few excellent sparks on here so just looking for a bit of advice. Have recently moved into a new house and the electric shower is terrible, water pressure is good though. I have a plumber coming Wednesday to advise if I could run one from the combi but I fear due to length of hot water run a meagre electric shower upgrade will have to suffice. Currently there a 9.5Kw one in, I would want to bump it to a 10.5Kw, anything would be better.
I've done some research but just looking to clarify to see if the current wiring is suitable, I just want to make sure things are safe.
So 10.5Kw/230V = 45.65A
I have a 10mm2 cable coming from the CU into a standalone 63A RCD, up some plastic trunking into the loft where is it not clipped onto anything then goes into the shower switch then from there down a cavity wall into the shower. The run from the CU to the shower is approx 8 metres.
There was some insulation in the loft on top the cable which can be permanently moved on put under the cable. The ceiling and walls are lath and plaster. I would say there is no insulation in the cavity wall based on the other walls having none but I cannot confirm. Which reference method should I use to determine the cable rating?
It wouldn't be a huge deal to replace the cable with 16mm2, but wouldn't that be hellish to terminate in the switch and shower? FYI I am pretty happy doing a bit of wiring usually but will probably have a spark deal with a shower if that's the way I have to go.
Thanks,