Not sure if this is the right place for this
Looking for recommendations for a company to design and install a control panel to be able to dose oxygen into a water stream. It's got to be flow proportional to the flow
Depends how accurately you want it - I’ve done some work with mass flow meters to dose various chemicals/gases (anmmonia and nitrogen mainly, but I’ve done others as well) into furnaces. You send a 4-20 or 0-10v signal out (or do it via comms) and the flow meter gives a corresponding signal back of actual flow. I think you can get cheaper versions that aren’t as accurate as mass flow, but they might be “good enough” for what you want. As always it comes down to cost - mass flow meters are quite pricey but the savings in gas might mean that’s not an issue.we are currently dosing it as a fixed flow of oxygen via 4 regulators, each one switching in via a solenoid as the flow increases.
we have a proper flowmeter for the water flow with 4-20ma output, and rotameters on each regulator
its worked like that for the last 30 years but our lot want a bit more exacting control
the electric side isnt a problem, we can do the plc control... just need to control the gas flow and have some feedback as to what its doing
No, you would need another sensor for that - mass flow is just an accurate dosing device, which I think is what the op wants. If you wanted to close the loop you could add a dissolved oxygen sensor I guess (I’m not a process engineer, so I don’t know if it would work), but from what I understand he just wants an accurate method of dosing.Does the mass flow sensor give the dissolved oxygen in the water ?
That's what I thought.No, you would need another sensor for that - mass flow is just an accurate dosing device, which I think is what the op wants. If you wanted to close the loop you could add a dissolved oxygen sensor I guess (I’m not a process engineer, so I don’t know if it would work), but from what I understand he just wants an accurate method of dosing.
If you want to have a closed loop then PID times can be tricky for dosing, I did one a few years back that went into an effluent stream and holding tanks - when you dosed the chemical it took 2 days for any effects to be measurable….might not be the case here of course