a friend of mine has bought a building to use as a workshop, and has asked me to cast my eyes over the electrics in an unofficial Cappasity.
As the building was built and wired before I was born I've never came across wording this old in an industrial setting.
At first I was very alarmed as there is no earthing but as I looked in to it a it more, every thing is wired in steel conduit all steel enclosures and steel DB's. All be it old cartridge fuse DB's with ceramic holders.
There has been a RCD fitted to the supply between the meter and the buss bar enclosure that feeds fused disconectors witch in turn feed various DB's etc.
The earthing for the water and gas has been brought up to date, I'm guessing at the same time the RCD was fitted. The building uses a TN-S earthing system.
Personly if it where me I would re wire just because of the age of the instillation, witch I have recommended but he wants to know if it's safe to use for the time being and do a rolling rewire, obviously subject to testing its hard to determin.
Basically was / is an all steel installation with no separate CPC acceptable / common place?
As the building was built and wired before I was born I've never came across wording this old in an industrial setting.
At first I was very alarmed as there is no earthing but as I looked in to it a it more, every thing is wired in steel conduit all steel enclosures and steel DB's. All be it old cartridge fuse DB's with ceramic holders.
There has been a RCD fitted to the supply between the meter and the buss bar enclosure that feeds fused disconectors witch in turn feed various DB's etc.
The earthing for the water and gas has been brought up to date, I'm guessing at the same time the RCD was fitted. The building uses a TN-S earthing system.
Personly if it where me I would re wire just because of the age of the instillation, witch I have recommended but he wants to know if it's safe to use for the time being and do a rolling rewire, obviously subject to testing its hard to determin.
Basically was / is an all steel installation with no separate CPC acceptable / common place?