Hello Wyn,
17Kw? that is nearly 90 amps at 240 volt at 0.8 power factor. Not suitable for a 6mm cable?
Alec
Hello Jugs,
"are the input figs correct"
That was the point of my last post, by the way you haven't considered power factor in your calculation, at 0.8 the full load at 17Kw would be nearer 51 amps, so 6mm would be small for 415 supply as well.
Alec
cheers for your help i was planning on running this on 240v single phase and planning on putting in a decicated supply for it my mig and compressor put still not sure was to do i was going to use a 32 amp plug on it and put a 40 amp breaker in for it what do you guys think
It will need much more than a 20A breaker. I think its time to get a sparky in for this one.[/QUOTE]
Ditto a NICEIC approved one.
good luck
Hello Jugs,
"NICEIC", being lazy I know, i could look it up but what is that?
Alec