Hyundai generator has run fine for 4 years (serviced annually) powering lighting, kettle etc. at the stable then last week lost output voltage completely, normally it would point to a failed AVR, but a few hours online research makes me wonder if it's the rotor at fault?.
Generator with test points marked (AVR disconnected for tests)
VAC readings were as follows:
1 - 2 6V, 3 - 4 6V, 1 - 4 12V, and 5 - 6 18V
From what I have read/watched, anything over 10V across brushes (5 - 6) points to a duff rotor? brushes and slip rings are in good condition. A failed rotor would make repairs uneconomical so any advice or more tests to carry out would be appreciated.
Section of circuit diagram
Cheers.
Generator with test points marked (AVR disconnected for tests)
VAC readings were as follows:
1 - 2 6V, 3 - 4 6V, 1 - 4 12V, and 5 - 6 18V
From what I have read/watched, anything over 10V across brushes (5 - 6) points to a duff rotor? brushes and slip rings are in good condition. A failed rotor would make repairs uneconomical so any advice or more tests to carry out would be appreciated.