Hello everyone,
I have a question about flex size and circuit protection
The triphase circuit in my workshop is fed from a 20A d curve mcb ( there is also a 30mA rcd before).
It then passes through 7m of 2.5mm wire in conduit to feed an isolator/two 16A sockets.
These will go to a 7.5hp motor and a 4hp motor for two wood machines. Only one will be in use at a time.
My question is this: is it ok to use 1.5mm2 flexes (h07-rn, 3m long)?
Do the downstream 10A and 6.5A motor overloads protect this smaller size of flex, or should I go for 2.5mm2?
I ask because i have the thinner stuff here already... but will buy thicker if needed...
thanks!
I have a question about flex size and circuit protection
The triphase circuit in my workshop is fed from a 20A d curve mcb ( there is also a 30mA rcd before).
It then passes through 7m of 2.5mm wire in conduit to feed an isolator/two 16A sockets.
These will go to a 7.5hp motor and a 4hp motor for two wood machines. Only one will be in use at a time.
My question is this: is it ok to use 1.5mm2 flexes (h07-rn, 3m long)?
Do the downstream 10A and 6.5A motor overloads protect this smaller size of flex, or should I go for 2.5mm2?
I ask because i have the thinner stuff here already... but will buy thicker if needed...
thanks!