Hi Guys
Went out to look at a job today, a 3ph generator 15-20 kva, running some submersible pumps and the two rcds I think one was 100ma and the other was 30ma on the genny were tripping, the genny is 3ph +1ph and earth and is earth grounded by an earthing rod, the output is 5pin but only 4 core cable is used which is connected to a panel with three 3ph mcb breakers then off to three seperate pump control panels, I isolated it to one pump, well the control panel actually, I disconnected the pumps and float switches but the panel was still tripping the rcd, when I looked closer the incoming earth was connected to the neutral connection on the 4p isolator!!, but not the boxes earth lug, in the control panel there is some 240 single phase control gear, timers etc, the guy that designed the panels said it did not matter as earth and neutral is bonded. I said yes but not after the rcd surely.
The thing is this has worked for months like this. I tried to explain as the 240 1ph unit operated it was 'liveing' up the boxes earth by using the earth as a neutral return to the genny.
The thing is they have just put a new main supply for the job to save having the genny, but only 3ph +earth, no neutral. I said to the boss I was disconnecting the genny for safety reasons. I said that the panels would need at least a 415 -240 tranny but then the neutral would be 'floating', could this cause problems with rcd's etc or would it be better to have a 415 to 240 but centre tap it and ground the centre ?? to give a more reliable neutral?
Went out to look at a job today, a 3ph generator 15-20 kva, running some submersible pumps and the two rcds I think one was 100ma and the other was 30ma on the genny were tripping, the genny is 3ph +1ph and earth and is earth grounded by an earthing rod, the output is 5pin but only 4 core cable is used which is connected to a panel with three 3ph mcb breakers then off to three seperate pump control panels, I isolated it to one pump, well the control panel actually, I disconnected the pumps and float switches but the panel was still tripping the rcd, when I looked closer the incoming earth was connected to the neutral connection on the 4p isolator!!, but not the boxes earth lug, in the control panel there is some 240 single phase control gear, timers etc, the guy that designed the panels said it did not matter as earth and neutral is bonded. I said yes but not after the rcd surely.
The thing is this has worked for months like this. I tried to explain as the 240 1ph unit operated it was 'liveing' up the boxes earth by using the earth as a neutral return to the genny.
The thing is they have just put a new main supply for the job to save having the genny, but only 3ph +earth, no neutral. I said to the boss I was disconnecting the genny for safety reasons. I said that the panels would need at least a 415 -240 tranny but then the neutral would be 'floating', could this cause problems with rcd's etc or would it be better to have a 415 to 240 but centre tap it and ground the centre ?? to give a more reliable neutral?