Can anyone help quickly.
I have a 240V single ph supply, live goes to 0V on transformer, neutral input to 240V on transformer. This is untouched and as supplied.
One output labelled 110V gives out 126V
The other output labelled 0V gives out 252V
Reckon transformer shot?
Without power feed connected transformer hums away. Soon as a connection to the 0V output is made it throws the main RCCB in consumer unit but no fuses.
Thanks Jon.
I have a 240V single ph supply, live goes to 0V on transformer, neutral input to 240V on transformer. This is untouched and as supplied.
One output labelled 110V gives out 126V
The other output labelled 0V gives out 252V
Reckon transformer shot?
Without power feed connected transformer hums away. Soon as a connection to the 0V output is made it throws the main RCCB in consumer unit but no fuses.
Thanks Jon.