No, not sections. It is for the house extension on a sloping site. semi underground garage and retaining wall.Layers....do you mean sections?
Might depend on what it's for....for my flat pack garage it has a raft that's steel reinforced and was poured in 2 sections.
Bob what sort of distance can they pump when the pipes are laid on the ground ..80m ????Better in one. Concrete pump? they are a very cost effective way of transferring large amounts of concrete.
Bob
I know this would be the preferred option, and it will be needing to be pumped anyway, but this involves the lane being blocked for several hours, and will need at least three mixers worth.Better in one. Concrete pump? they are a very cost effective way of transferring large amounts of concrete.
Bob
They can pump that far I think. They ban also pump vertically. If you want much more than a cubic metre, is in not worth the hassle of wheelbarrowing it, even less mixing it yourself. Ready mix costs just over half what it would cost to buy the materials to mix yourself, with no effort. Its a no brainer.Bob what sort of distance can they pump when the pipes are laid on the ground ..80m ????
Yes, it will be worth the effort. If it were an easy site, and the hole not overdug, I would not be asking the question !The question i'd be asking...is it worth the effort?
I would think that whoever is doing all the calculations for the structural elements would probably be best to advise.
Have you got a photo of the engineers drawings?I know this would be the preferred option, and it will be needing to be pumped anyway, but this involves the lane being blocked for several hours, and will need at least three mixers worth.
The excavation was done years ago and never finished. It was also overdug, so I need to raise the level somewhat. It is on pure chalk, so I thought maybe I could cast the understructure more or less on the surface of existing surface, then do some infill and then pour the slab over this.
Structural engineer has massively overspecified because of this, but am hoping for some input before I go to building control with it.
What a lovely easy site. If only ........Yes, no problem pumping 50mts + even with a small rig. They are cheaper to use than labour and dumpers.
Bob
View attachment 532005
View attachment 532006
They are part of the plans, but will try and sort something outHave you got a photo of the engineers drawings?
Dont know if you can figure this out.Have you got a photo of the engineers drawings?
Any" joints" in the slab would be horizontal.
Yes, the joints would have projecting rebar, actually the top of the horizontal foundation beam cage.Will the joints have reinforcing projecting from them (i.e. vertical bars)?
On any building site which is supervised, the laitance form a concrete construction joint needs to be removed before pouring on top of it. This is as much to stop moisture tracking along the joint and corroding the reinforcing as it is for structural strength.
Traditionally this was done by scabbling, and since HAVS received more focus, that is now frowned upon. Instead, a retarder is applie to the joint and it is jet washed or wire brushed the next morning.
As above, show the reinfocing drawings and indicate on them where the construction joints would be. Just the structural drawings alone, without the rebar ones will not give you the best answer.
---
If you are pumping 80m long, you have to allow for the concrete in the pipe when measuring. You also have to dispose of that concrete somehow. The pump will need somewhere to wash out - we used to make a tray out of four scaffold boards and line with 1200 ga. DPM.
If you want a good job, tell the concrete supplier it will be pumped and buy a pumpable mix. Otherwise, the only way to make it pump is to add excess water, which compromises the strength.