Tell my test meter thatYes too, although in theory we are now on 400V...
You read it right, but isolating doesn't mean it simply outputs what you put in.If it’s an isolating transformer I would expect the output to be 415v? Or did I read it wrong?
Connect it up
Measure output volts
Move input if not within spec
Re measure output
Move other way if still wrong
Job jobbed.
Is it just an isolating transformer, no step up/down? Did you try it on -15?I did measure the output volts with input on both 0v and +15v and the output was the same![]()
What was the output voltage?I did measure the output volts with input on both 0v and +15v and the output was the same![]()
Yes it's for control voltageIs it just an isolating transformer, no step up/down? Did you try it on -15?
I’ve only ever used step down for controls voltage so 230/415 in and 110 out - the different inputs always made a difference to the output when setting those up, maybe it doesn’t make a difference on a plain isolating transformer?
I would have thought it would do though![]()
Didn't make a note but 115.-- something volts on either setting.What was the output voltage?
400/415 is less than 4% difference, so isn't going to have much noticeable effect on lower voltage outputs.
Bigger issue is possibly the transformer running hotter due to a slightly higher voltage than the actual rating, but I'd guess there is a fairly large margin before it became a problem.
I’d try it on all 3 connections - if negligible difference then don’t worry too much about it.Didn't make a note but 115.-- something volts on either setting.
So i should have it on the -15v setting you're saying?
I wish RS' documentation was a bit clearer
I'd have expected a bit more variation on a 115volt output, but it could be a saturation issue limiting the voltage.Didn't make a note but 115.-- something volts on either setting.
So i should have it on the -15v setting you're saying?
I wish RS' documentation was a bit clearer
is that it means the +/-15 is relative to the 0V point.Standard primary winding 0-230-400VAC with a +/- 15V adjustment possibility around 0.